marke Posted February 3 Report Share Posted February 3 The Control Word is set by serial communications from the PLC. These are the values to insert into the control word to RUN Forward, RUN Reverse, STOP and RESET the drive over the Modbus TCP network. // Run Forward If ((RunForwardIn = True) and (RunReverseIn = False)) then ControlWord := 16#047C; End_If; // Run Reverse If ((RunForwardIn = False) and (RunReverseIn = True)) Then ControlWord := 16#847C; End_If; // STOP If ((RunForwardIn = FALSE) (*And (RunReverseIn = False)*) And (ResetIn = False)) then ControlWord := 16#043C; End_If; // RESET If ((RunForwardIn = FALSE) (*And (RunReverseIn = False)*) And (ResetIn = True)) then ControlWord := 16#04BC; End_If; Sample Horner PLC code in CScape 10 SP1 attached. tcp demo.csp Mark Empson | administratorSkype Contact = markempson | phone +64 274 363 067LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters Link to comment Share on other sites More sharing options...